Thread Rating:
  • 0 Vote(s) - 0 Average
  • 1
  • 2
  • 3
  • 4
  • 5
Using 2 30 amp shore power cords in lieu of a single 50 amp one
#9
You are correct your 50amp 240 volt cable is split into 2-circuits at the main electrical panel, each circuit capable of providing 120 volts @ approximately 30 amps... You also have a single 30 amp 120 volt circuit and when used powers both circuits but you are now limited to a total of 30 amp draw. When using the single 30 amp that is bridged you must limit yourself to drawing no more than 30 amps total or the main breaker will pop. On my 38 Open the main breaker for the 30 amp service is located outside in the cockpit near the connection for the dockside cable. M2C
Reply


Messages In This Thread
RE: Using 2 30 amp shore power cords in lieu of a single 50 amp one - by ReelMagic - 08-17-2018, 11:01 AM

Possibly Related Threads…
Thread Author Replies Views Last Post
  1997 4000 express shore power issue Salty0ne 10 4,354 03-31-2025, 08:27 PM
Last Post: jclark003
  Fridge and freezer isotherm combo only work with shore power or genset Toyoda 2 3,022 07-26-2023, 03:55 PM
Last Post: Sapphire
  No power to dash Mydiamond 5 4,472 05-07-2023, 07:52 PM
Last Post: Mydiamond
  [Tiara Convertible] Light with No Power Question T.Roy 3 3,026 06-14-2022, 01:32 PM
Last Post: Misdirection
  No shore power to one side of AC panel wcish 3 3,322 05-01-2022, 05:05 PM
Last Post: eric_nelson



Users browsing this thread: 1 Guest(s)
Advertisements

Latest Threads
3500 Open deck lift piston
Last Post: drmiagi11
Yesterday 12:51 PM
» Replies: 3
» Views: 1015
Hot Engine Room
Last Post: Nelsond
11-04-2026 11:36 AM
» Replies: 0
» Views: 56
Anyone using a cordless robot on a Tiara...
Last Post: thomasbrown
11-03-2026 05:08 PM
» Replies: 0
» Views: 58
Anyone using a cordless pool cleaner wit...
Last Post: hiccup
11-02-2026 01:18 PM
» Replies: 1
» Views: 92
Replacing the head on a Tiara 3100 — do ...
Last Post: hiccup
11-02-2026 01:17 PM
» Replies: 1
» Views: 79