Tiara Open Bow shore power 50 amp
#1
Greetings,

I have a 2002 4100 open and it has a 50 amp shore power receptacle in the bow.  I hooked up a 50 amp 125/250v shore power cord and I'm not getting power to the service panel in the salon.  I confirmed the breakers are on at the dock and the bow receptacle.  I used my neighbor's shore power and cord and still no power.

The boat has another 50 amp shore power connection with an automatic cord reel in the cockpit area.  Is there a switch somewhere on the boat that separates the two 50 amp shore power ports?

On a side note, the automatic shore power cord retractor does't work and I can't test this connection. Has anyone had issues with these too?  It has 13.5v at the motor.  I assume the motor is bad but from the previous owner, it was never used.

Thank you!!!!
Like Post Reply

#2
Can you take the 50 amp cord you planned on using for the bow and plug it into the retractable one (while retracted) to test that circuit?

I'm not familiar with that model, so I'm not sure if the transfer is supposed to be automatic or by a manual switch somewhere.

Sent from my XT1635-01 using Tapatalk
Like Post Reply
#3
I own a 2003 38 Open with the auto coiler and assume you are aware there is an auto stop (in limit switch) when the cable is fully retracted (unit is a cablemaster built by Glendenning).... There is a micro switch that stops retrieval to ensure no damage is done when fully retracted. I've attached a portion of the owners manual..... It's possible the limit switch is not working or is preventing the system from working See if it helps to understand the problem.  Google "glendenning cablemaster manual" for a full copy..

[-] The following 1 user Likes ReelMagic's post:
bsause (11-23-2018)
Like Post Reply
#4
Thanks for the advice. I'll try to connect the cockpit cable and see if that works.
ReelMagic, great information. I downloaded the manual and this will be extremely helpful.

Thank you both!!!!
[-] The following 1 user Likes hookup44's post:
bsause (11-23-2018)
Like Post Reply
#5
I have a 50A inlet in the bow locker on my 52. I runs to a Charles automatic transfer switch in the ER. You most certainly have some kind of auto or manual transfer switch or plugging in one cord would energize the other and sparks and shocks would certainly follow. If one 50a inlet works and assuming you don't have multiple 50a inlet selectors on your AC distribution panel, I would be in search of the transfer switch. Following the cable from the cablemaster tub inside the boat will eventually point the way. If not obvious in the ER maybe look behind the AC panel (turn off shore power first).

My transfer switch has a manual override on it in case the automatic system fails. It may be as simple as that. Either way let us know what you find. Best of luck.
Like Post Reply
#6
JClark003, thank you for the lead. I will be at the boat on Monday and report back.
Have a great weekend.

Tim
Like Post Reply
  


Possibly Related Threads...
Thread Author Replies Views Last Post
  1997 4000 express shore power issue Salty0ne 10 3,979 03-31-2025, 08:27 PM
Last Post: jclark003
  Fridge and freezer isotherm combo only work with shore power or genset Toyoda 2 2,874 07-26-2023, 03:55 PM
Last Post: Sapphire
  No power to dash Mydiamond 5 4,249 05-07-2023, 07:52 PM
Last Post: Mydiamond
  [Tiara Convertible] Light with No Power Question T.Roy 3 2,886 06-14-2022, 01:32 PM
Last Post: Misdirection
  No shore power to one side of AC panel wcish 3 3,173 05-01-2022, 05:05 PM
Last Post: eric_nelson



Users browsing this thread:
1 Guest(s)

Bow shore power 50 amp00