01-24-2021, 10:38 PM
(01-24-2021, 09:47 PM)jclark003 Wrote: Welcome to the forum
So you have 120 VAC at breaker but not at hot lead termination at charger? So probably a break somewhere in the circuit.
You can reach out to Tiara with your HIN and they will send you a wiring schematic. But I would be surprised to learn of an inline fuse or something that could interfere with the hot leg of the circuit. Unusual to have a wire break as described/suspected. Sometimes corrosion works it's way under the insulation, gets hot and the wire breaks internally. I would recommend probing the wire about 6 inches in from each lead. Otherwise get some marine grade wire and pull a new cable. Shouldn't be that difficult to get from charger to distribution panel. Good luck
Thank you for the post. I agree with your assessment that it is unlikely a wire break. I followed from the charger as far as I could and it is very well protected. I actually have the wiring diagram (to large to attached) and from what I can tell (I’m not an electrical expert) the neutral and ground go to a buss bar and the lead is direct to the panel. I will try probing the wire and see if I can isolate a break. There is an option to pull a wire or jump from a nearby outlet. I was just hoping to keep it factory. I plan on reaching out to Tiara tomorrow and see if they have seen this issue before.