Westerbeke gas generator
#1
Hi all, having an issue with my Westerbeke gas generator. When i go to start it the 8amp fuse on the generator control panel blows. I have bypassed the oil pressure switch, water temp switch and high exhaust temp switch, fuse will still blow. i have a short somewhere and cannot locate it. if I disconnect the remote switch harness the fuse will not blow but the genny will only stay running while holding the ON switch on. Very confusing....any ideas out there? i cant get a mechanic to look at it, most dont want to work on GAS generators.
Like Post Reply

#2
There are alot of reports and resolutions of the 8 amp fuse blowing for this generator over on The Hull Truth and iBoats.

But did you just jumper the temp and Oil pressure sensors or did you disconnect them and jumper them? The sensors themselves can go bad and cause a short.

Sent from my SM-A505U using Tapatalk
Like Post Reply
#3
Thanks for your reply Misdirection, I went back to bypassing the shut down switches and found it to be the water temp switch, I did need to jump because it is a closed switch, I also needed to have the remote harness hooked up to complete the circuit. Got the new switch and installing today, then the boat is ready to put up for sale, new to us boat coming soon!
Like Post Reply
#4
(08-24-2020, 12:27 PM)Misdirection Wrote: There are alot of reports and resolutions of the 8 amp fuse blowing for this generator over on The Hull Truth and iBoats.

But did you just jumper the temp and Oil pressure sensors or did you disconnect them and jumper them?  The sensors themselves can go bad and cause a short.

Sent from my SM-A505U using Tapatalk

Would you have a link on how to bypass the sensors? My generator runs for about 20 to 30 minutes and then shuts down. It is;t running hot or overheating base on temps from temp gun.  Thanks in advance.
1988 33 Open - 454 Crusader - Trophy Hunter

[Image: NBvUYCDdQEqZfboL8]
Like Post Reply
#5
I would start by finding your generator at Westerbeke and downloading the troubleshooting and electrical diagrams. I believe one of those two will provide instructions on how to locate temporarily jump each sensor.

[Only registered and activated users can see links Click here to register]

Sent from my SM-A505U using Tapatalk
[-] The following 1 user Likes Misdirection's post:
ardoski14 (09-01-2020)
Like Post Reply
  


Possibly Related Threads...
Thread Author Replies Views Last Post
  2001 3100 open generator runs but doesn't generate electricity lakesidevu 5 2,215 11-14-2025, 01:01 PM
Last Post: hiccup
  2006 3600 Sovran Generator Battery location Final Pursuit 0 628 08-09-2025, 07:49 AM
Last Post: Final Pursuit
  [Tiara Open] Westerbeke 5.0 BCDB jsheerin 3 1,978 04-26-2025, 02:00 AM
Last Post: Roweje
  Westerbeke Generator no start Joeboch348 5 3,348 05-30-2024, 09:58 PM
Last Post: Joeboch348
  Generator Usage Jayr 4 4,197 08-17-2020, 09:47 AM
Last Post: Jayr



Users browsing this thread:
1 Guest(s)

Westerbeke gas generator00